simulation results do not match journal references

    • Alwan Hibatullah
      Subscriber
      I'm doing a simulation of an electric motor cooling system using Ansys Fluent. there are three components in my simulation, namely the stator, water cooling jacket, and helical coil as the fluid domain. I use a tetrahedral mesh in this simulation with y + = 1. for boundary conditions at the inlet is the inlet velocity and outlet is the outlet pressure, and in the stator section a constant heat flux of 3500 W/m2.K is given in laminar flow, or can be seen in the following picture of my geometry;
      when the simulation is finished running and I analyze the results, the Nusselt value that I get from the calculation does not match the validation equation from my journal reference. even though in my reference journal, the mesh elements used and y + used are the same and larger. however, when I simulate the helical coil alone without jacket and stator, the results I get are appropriate and correct. then when I move the mesh settings and helical coil setup to the intact cooling component, the results are still wrong.
       
      in addition I have tried to smooth the mesh and thicken the inflaction layer, but the results are still not appropriate. is my mesh still not smooth enough or is there a problem in other parts? please can anyone help my problem?
    • Rob
      Forum Moderator

      /forum/forums/topic/simulation-results-do-not-match-the-validation-equation/

    • Rob
      Forum Moderator

      Do the fluxes agree between the two models? What boundary conditions have you used? 

      • Alwan Hibatullah
        Subscriber
        Hello Rob, thanks for reply

        yeah. For the heat flux on the helical coil, I took the value when simulating the electric motorbike cooling system, so that it can be used as the temperature value on the wall and outlet as it should be, for the helical coil.
         
        then what does the boundary condition mean, what do I use?
    • Alwan Hibatullah
      Subscriber

      and for meshing on the helical coil section it has the size as shown in the picture. with y+ = 1 at Re 500 with 6 mm hydraulic diameter

      then for the boundary conditions as I mentioned using velocity inlet, outlet pressure, constant heat flux on the stator, and adiabatic jacket walls. for a screen shot on fluent as shown below

    • Rob
      Forum Moderator

      And how does the heat balance look over all of the walls? Why have you got so many contact regions?

    • Alwan Hibatullah
      Subscriber

      I don't know. when I use common meshing, the boundary condition will be like that. the interface part has another name such as coil-contact-region-src has another name which is wall-20 and so does the other interface.

      But when I use fluent special meshing (fluent with meshing), the boundary condition naming becomes simpler, as in the following picture

      although the results between the two boundary conditions are still the same. still not in accordance with validation. so is there an error in the boundary conditions or in other parts?

    • Rob
      Forum Moderator

      Assuming heat going in is the same as heat coming out and residuals are good then the model is likely correct. Whether the boundary conditions you set are appropriate is a different question, and one I can't easily answer. 

      The model with the conformal mesh is the one I'd focus on. How does the heat flux in the full model compare for each surface to the simple model?

    • Alwan Hibatullah
      Subscriber

      There should be no problem with the boundary conditions, because the simulation I ran was just like any other simple simulation.

      In the comparison of the full model and the simple model, I took the heat flux data received by the helical coil during the full model simulation. then I tried to simulate the simple model with the heat flux data. so you could say that in the full model and the simple model, the helical coil has approximately the same heat flux, so the temperature at the coil wall and outlet between the two models should have approximately the same value.

      Then what other parts should I pay attention to besides the meshing?

    • Rob
      Forum Moderator

      Did you take the heat flux as an average value or the heat flux (or temperature) profile? 

      Meshing should be about right, if the resolution isn't quite there you may see a few % difference. I'd then focus on the Nusselt Number definition to make sure you're using the correct reference values. 

    • Alwan Hibatullah
      Subscriber

      i use the average heat flux value along the wall of the helical coil

      then for the Nusselt value, as validation I use the Manlapaz and Churchill correlation equations for helical coils in laminar flow. for example, for Re 500 the Nusselt number should be around 12, and for simple models the Nusselt number should be correct with an error below 10%. but for the full model, the value of the Nusselt number that I get ranges from 2, so it has a high error.

      for the record I did the analysis using excel, so when changing the model, I only changed the temperature values on the walls and outlets, so there shouldn't be any errors in the analysis calculations

    • Rob
      Forum Moderator

      Did you use the Nusselt Number value from Fluent, or take identical data to the correlation? 

    • Alwan Hibatullah
      Subscriber

      I took identical data from the analyzes using inlet, wall, and outlet temperatures. which I then compared with the correlation equation

      if I take Nusselt number data from fluent, the value is very high, which is above 100

    • Rob
      Forum Moderator

      The built in Nusselt Number uses a reference value - it can be negative too. 

      Check which wall temperature you used: the "normal" one plotted on the wall may not be what you're after. 

    • Alwan Hibatullah
      Subscriber

      I've tried using a reference value, but the result is the same. Or maybe there is something wrong in entering the value? because to be honest I'm still a bit foreign to reference values

      then for the wall temperature you mean which one should I take?
      because after I compared the full model with the simple model, both have more or less the same outlet temperature, but have very different wall temperatures

    • Rob
      Forum Moderator

      Have a look at the definitions, you then need to pick whatever matches what you're comparing with. 

    • Alwan Hibatullah
      Subscriber

       

      definition in the boundary condition section? or where do you mean

      I took temperature data on the wal helical tube, both the full model and the simple model. but on the full model the temperature of the wall helical tube is much higher. or is there a specific way for data retrieval on walls that are attached to each other?

       

    • Rob
      Forum Moderator

      Field variables, https://ansyshelp.ansys.com/account/Secured?returnurl=/Views/Secured/corp/v232/en/flu_ug/flu_ug_FlowVariableDefs.html  but also have a look at where (and what) you're adding on the thermal bc. Also, where it's going. 

      A heat flux boundary will adjust facet temperature to enforce the flux, temperature will adjust the flux. So, with flux it's possible to get very high (or low) temperatures depending on the flow field: with temperature the flux can be non-physical. 

    • Alwan Hibatullah
      Subscriber

      where is the destination of the link? because it takes an account number but I use ansys sutdent

      so if I give a constant flux to the stator (see picture above), where will the heat flux propagate to the helical coil right? so that the helical coil will also be exposed to a constant flux with a greater value than the stator because of its smaller surface. then with the same heat flux, why is the temperature value of the helical coil in the full model and the simple model different between the two modes?

    • Rob
      Forum Moderator

      Click on Help in Fluent & paste the link into the browser that opens. 

      You're adding W/m2 as a flux. If you have a difference in surface area that can cause a slight error, the other issue is uniformity of the flux. 

    • Alwan Hibatullah
      Subscriber

      then paste where? because I still enter the registration form

      the meaning of this flux uniformity is that the flux in the stator and helical coil must have the same value?

    • Rob
      Forum Moderator

      Click on Help in Fluent. That should open a web browser. In a tab in that browser paste the link I provided. Assuming you don't default to private/incognito that should take you to where I was linking. 

    • Alwan Hibatullah
      Subscriber

      oh yes it can. but i'm sorry, I still don't understand what you mean or what you want to show me when I open the link. what does it have to do with the temperature on my helical coil wall which is still wrong

    • Rob
      Forum Moderator

      You asked about the wall temperature - there are several. 

    • Alwan Hibatullah
      Subscriber

      oh yeah i got it. but I have tried all the variables for wall temperature like Wall Temperature, Wall Temperature (Thin), Wall Adjacent Temperature, static temperature, and total temperature, but they all have the same result

    • Rob
      Forum Moderator

      Then there's likely something not being accounted for in the model set up. 

    • Alwan Hibatullah
      Subscriber

      usually what is missed when preparing a model for a cooling system case like this?

    • Rob
      Forum Moderator

      Usually it's a boundary setting or reporting issue. 

      Sketch out the layers of boundaries (hot bit, casing coil etc) as a list & link where the two models are common. Check what thermal load is then applied: ie W/m3/s or W/m2 etc and then look to see if the flux in the model ties up with what you expect. For a steady system Watt (I like bad puns) goes in must come out, so also check where heat leaves the system. 

    • Alwan Hibatullah
      Subscriber

      I'm sure that the heat load uses W/m2.K and how to make sure the heat entering is the same as leaving, is it by selecting all the boundary conditions and calculating the heat?

    • Rob
      Forum Moderator

      Yes, heat in, and heat out. But where you have a face common to both models check they're the same. 

    • Alwan Hibatullah
      Subscriber

      yes there is no problem when I check through the mass balance

      then there are those who say that it is the relationship or interaction from solid to fluid that is problematic. what does that mean and how to check and fix it

    • Rob
      Forum Moderator

      Fluid-solid thermal tends to be an issue when the mesh is too coarse. 

    • Alwan Hibatullah
      Subscriber

      this means having to fine-tune the meshing on the interconnected parts of the wall?

       

    • Rob
      Forum Moderator

      Not normally, if you use inflation and think about mesh resolution it's usually pretty hard to get the solution badly wrong. 

    • Alwan Hibatullah
      Subscriber

      here I use a fairly small mesh size in the fluid domain and have tried using quite a lot of inflation layers with y+ = 1, but the results are still not right. however, for the mesh in the solid domain, I still have quite rough settings, and not as small as in the fluid domain.

      ah for the record, in my reference journal they use y+ = 5, with a maximum element mesh of 5 million. I've matched them as closely as possible to my references, though I don't know how small their smallest mesh is in the solid domain.

    • Rob
      Forum Moderator

      A few % error may be down to a marginal difference in mesh. A much larger difference is more likely down to a setting: be that boundary condition or geometry dimension. 

    • Alwan Hibatullah
      Subscriber

      I've seen several video tutorials on YouTube that have similar cases, but the fluent setup settings that I see are not too different from mine

      Is there another tutorial that has similarities so that it can be used as a reference? because I haven't found anything really similar, like a fluid that functions as a coolant for the solid domain with a heat flux heat source

    • Rob
      Forum Moderator

      I don't think so, all the tutorials I can point you at at in Fluent's Help system or Learning on here. Have you compared all of the common faces in each model to see where differences come in? 

    • Alwan Hibatullah
      Subscriber
      yes it has, and I haven't found a model at least similar to mine. most of those using helical coils are heat exchangers with two fluids, and unlike mine which is a transfer of heat from solid to fluid