Ansys Employeedepending on the initial temperature field, it may happen the convergence criterion for scaled residuals is already satisfied during the first iteration. This doesn't necessarily mean the solution is converged. For solution to be declared converged, three conditions must be satisfied:
1) residuals drop below a specified threshold,
2) global balance of mass and heat is achieved: report - fluxes. The imbalance must be < 1% of the smallest flux through a boundary
3) monitors of interest are not changing from iteration to iteration
In your case, either reduce the convergence criterion, say, by an order of magnitude, or simply set the convergence criterion to none and iterate until 2) and 3) are satisfiedÂ
-
November 23, 2018 at 5:18 am
-
November 27, 2018 at 11:13 am
seeta gunti
Ansys EmployeeHello,
If you got the solution, please make this thread as resolved.
Thanks,
Seeta
Â
-
November 29, 2018 at 8:16 pm
suraj9735
SubscriberThanks for replying me..!
I strange to see the solution converged in 2 iterations (in initialization only). So I curious to know how can I predict that particular model is going to converge in following no. of iteration.
BTW, I compare my model solution of Fluent with " steady state thermal analysis" of ANSYS Mechanical. And I found a similar result. But there is some difference.
Mechanical result
Â
Fluent result
Â
I use total power 120 W. Heat flux report shows -116.3293 W. still there is missing 4W. My model has only solid and try to solve energy equation. Could you please recommend me what method in Fluent is suitable for this model?
2) I can also solve this model in Mechanical but I try to solve in Fluent because I think it has the more advanced function that will help me in further modelling to control the temperature of this model.
-
November 30, 2018 at 5:51 am
Keyur Kanade
Ansys EmployeeIf it has only solids, please go head with mechanical.Â
-
December 2, 2018 at 8:44 am
suraj9735
SubscriberI don't know how to work with command in Ansys Mechanical, That is why I am using Fluent because I know something about UDF and trying to write source udf.
-
December 3, 2018 at 10:00 am
seeta gunti
Ansys EmployeeHi Suraj,
Can you check all the positive and -ve values and calculate and compare with Net value.
-
December 3, 2018 at 5:48 pm
suraj9735
SubscriberThanks guys. I use "none" setting for residuals convergence and let it to converge till what I want. And it works!