October 16, 2022 at 12:25 am
grigorios.sergentanis
SubscriberHi everyone,
I'm relatively new at ANSYS. I've had success calculating leakage inductances/magnetizing inductances of transformers in maxwell 3D, as I could find material on the demo models. However, I need to also calculate parasitic capacitance (intra and inter winding), but I cannot figure out the best way to go forward with this. Has anyone done this successfully and is willing to share their ways?
Many thanks. -
October 25, 2022 at 5:31 pm
GLUO
Ansys EmployeeHello @Grigorios,
Electrostatic solver and transient A-Phi solver can do capacitance calulation. In electrostatic solver, you could right click parameter and assign matrix to the windings. In transient A-Phi solver, you could enable the matrix calculation, then assign matrix to the windings.
Regards,
GLUO
-
October 25, 2022 at 8:41 pm
grigorios.sergentanis
SubscriberHello @Gluo,
Thank you for taking the time to reply. I did find out about the electrostatic solver, but it didn't take into account the voltage distributions along the transformers windings.
I had a quick google for the A-phi solver and it seems ideal, since it does do that. I will test it in the next days.
Kind regards,
Greg
-
November 23, 2022 at 11:59 pm
mustafa ÜREN
Subscriberhello, can you share your transformer design file with me?
-
- The topic ‘Transformer Design – Parasitics’ is closed to new replies.
-